Davis
Member
- Location
- Washington
I am wondering how others see this situation.
Table 310.15(B)(6) list conductor types and sizes specifically for 120/240-volt, 3 wire, single phase dwelling services and feeders that carry the entire load of the dwelling unit.
In our state the circuit breaker on the generator is the required disconnect even if it is not specifically service rated. If the generator is readily accessable and located within site of the building the circuit breaker on the unit will suffice.
So the conductors that supply the load at the house are between the main disconnect on the generator and the panelboard which have the loads.
Home generators are classified Optional Standby Systems and as we know they are a feeder.
Also load shedding would have no bearing on the situation. If a generator fed an entire home regardless that some loads could possibly be shed makes no difference. It still is connected to the entire house load.
Example #1: The house has a 200 amp service, 1 200 amp panel.
20kW run to a 200 amp SE ( service enterance ) load shed transfer switch. Some loads are shed as necessary to meet Code.
The generator has a 100 amp CB. According to the table, #4 cu or #2 al is ok. All the conditions of Article 310.15B)(6) are met.
Example #2: the house has a 400 amp ( actually a 320 amp ) service, 2 - 200 amp panels.
20kW run to 1 - 200 amp SE transfer switch with only one panel connected at the house. The other panel is not backed up.
All the conditions are now NOT met and using the table would not be allowed. The generator is NOT now powering up the entire house.
How do others see this?
Table 310.15(B)(6) list conductor types and sizes specifically for 120/240-volt, 3 wire, single phase dwelling services and feeders that carry the entire load of the dwelling unit.
In our state the circuit breaker on the generator is the required disconnect even if it is not specifically service rated. If the generator is readily accessable and located within site of the building the circuit breaker on the unit will suffice.
So the conductors that supply the load at the house are between the main disconnect on the generator and the panelboard which have the loads.
Home generators are classified Optional Standby Systems and as we know they are a feeder.
Also load shedding would have no bearing on the situation. If a generator fed an entire home regardless that some loads could possibly be shed makes no difference. It still is connected to the entire house load.
Example #1: The house has a 200 amp service, 1 200 amp panel.
20kW run to a 200 amp SE ( service enterance ) load shed transfer switch. Some loads are shed as necessary to meet Code.
The generator has a 100 amp CB. According to the table, #4 cu or #2 al is ok. All the conditions of Article 310.15B)(6) are met.
Example #2: the house has a 400 amp ( actually a 320 amp ) service, 2 - 200 amp panels.
20kW run to 1 - 200 amp SE transfer switch with only one panel connected at the house. The other panel is not backed up.
All the conditions are now NOT met and using the table would not be allowed. The generator is NOT now powering up the entire house.
How do others see this?