Contractor proposes to use these:
Burndy: YF4/040UI

but I can't see where they are suitable for DLO cable. (nor can I see where they are not)

input appreciated.

They are a ferrule.

I suspect they are fine as a practical matter.

An inspector might note they are not listed and question their suitability.
 

templdl

Senior Member
Location
Wisconsin
Get a copy of UL486a and b which covers the listing requirements for breaker terminals. I believe this is a link to a PDF file for UL486 which covers type of wire and stranding, torque, eperature tests, pull tests, etc. When someone such as Illsco lists a lug this is what is required first then the device manufacturer must list their devise for use with that lug. This may not show the requirements for screw type pressure terminals.