sceepe said:You can't make a delta configuration with two elements (or a Y config for that mater).
In other words, connect it in open Delta, the way you'd connect two 208v 1-ph loads to a 3-ph supply.iwire said:I pictured two elements connected to phase B and one element apiece to phases A and C.
LarryFine said:This can be done as long as there is a way to supply the controlling components with separate supplies.
I mean they would need to be capable of that, and I said 'controls' and not 'elements' because I pictured the typical electro-mechanical thermostats, and not electronics. Follow me:iwire said:Why would the controls need separate supplies?
LarryFine said:With that in mind, to do what he asked, there would need to be a way to separate the elements and their controlling components, or at least one line side of them, which is how I ended up wording my post the way I did.
voltairzap said:We have an installation to connect a three phase water heater. the unit has two 4500 watt elements inside. We are to connect three legs of the incoming three phase with the center leg connected as a "common" between the two elements. What is the calculated amperage load for each leg if operated at 208 volts?
If this were single phase, then the center leg would be the sum of the other two legs. But with three phase power, shouldn't the "three phase factor" (1.73) be involved in the calculations for the "common" conductor?
John
I concur with sceepe...iwire said:I think we all have different ideas of what the OP has.
The only electric water heaters I have hooked up that 'alternate' elements are home units.
As this is three phase I take it to be a commercial unit which in my experience will run all the elements at the same time when needed.
If it is to be wired 3? in "open delta" configuration, what would be the advantage over 1?? It would certainly be a costlier installation, as 'stiff mentioned. Perhaps the manufacturer made wiring optional so one can balance panel loadingIf it were a three phase water heater it should have three elements.
Can you supply us with the nameplate info on the water heater so we can come up with exact numbers?
Smart $ said:I concur with sceepe...
Ummm... a good indication was the OP/thread title?three phase power to single phase water heater :wink:iwire said:The only person posting to this thread that has actually seen the unit said it's three phase.
As I don't have the power to see through the Internet yet I figured I would take their word for it.
But as long as you say it's not three phase it must be the fact. :grin:
The first question I would ask here is are the elements rated for full output at 208 Volts or are they 240 Volt rated elements that are intended to be connected to a 208 Volt supply?voltairzap said:We have an installation to connect a three phase water heater. the unit has two 4500 watt elements inside. We are to connect three legs of the incoming three phase with the center leg connected as a "common" between the two elements. What is the calculated amperage load for each leg if operated at 208 volts?....John
Smart $ said:Ummm... a good indication was the OP/thread title?three phase power to single phase water heater :wink:
voltairzap said:We have an installation to connect a three phase water heater.
iwire said:So unless the OP provides some more info we are left guessing.
diopmarilyn@bellsouth.net said:You Take 4500*3= 13500w
And You Dvide By 360v.=37.5a Since These Water Heater Came With 3sets 37.5*3=112.5a At125%=140.625a Required 150a Cb.
Corect Me If I Am Wrong
....the unit has two 4500 watt elements inside