Ok, time to put on your thinking cap. Forget the transformer DGA for now, why are you having multiple repeated fuse blowouts in more than one location?
Are these three-phase transformers? Is it the same phase fuse that fails every time at all locations?
What equipment is common to the phase that keeps blowing fuses?
Is the overall load on the service at each location balanced as closely as possible?
Have you tried putting data recorders on the secondary to see if there are loading issues?
Is it the same brand, size and type of transformer in all cases? Are they of the same "age" , i.e. possibly a bad batch of trannys from that manufacturer?
There are a lot of facts that need to be discovered or you will never end this problem.
I have many facts.
There are 3 car wash locations out of 11 total served that are having this issue. I have monitored at locations blowing fuses and at locations not blowing fuses. The loads are nearly identical (the customer is Mikes Carwash and the electrical design is cookie-cutter). All transformers are 3 phase 12,470 V Y-480Y/277 V 500 KVA and loaded up to around 400-450 KVA during business hours. Inrush currents amount to about 1/10th of what it would take to reach the minimum melt curve of the fuse (for the magnitude and duration of the inrush currents). I have not been lucky enough to be monitoring when a fuse blows. The vast majority of the load is 3 phase motors/compressors, so everything is balanced, and the monitoring data supports this claim.
In all occurrances where the phase is documented, B phase fuse is the one to blow. On the most recent occurrance, the trouble person attempted to replace the blown fuse and the fuse blew again almost immediately. The transformer and service conductors were tested for a fault, but nothing was found. Several hours later, the blown fuse was replaced again and this time it held (and has held for a few weeks now). To me, this points to heating, which points to something mechanical, like a connection issue. From monitoring data collected, the heating does not appear to be from loading. I have learned that the fuses are typically not properly torqued. Over- or under-torqueing can cause the fuse link connection to heat up and possibly blow prematurely.
The question remains: why is this only happening at 3 out of 11 seemingly identical locations both in terms of the customer load, and electrical system?
I need to try and run down information on the manufacture and age of the transformers. The locations having the issue were built at different years with a few years in between, same as the ones not having the problem.
We also have seen this issue come up at saw mills. The running theory is that there is something with a repetitive inrush current banging on those fuses, coupled with probable improper torquing, causing heating and possibly arcing and eventually fuse failure. At this point we are probably going to put in a 750 KVA transformer and call it a day.
I would appreciate any ideas at all.:-?