CobyRupert
- NY
Similar to a recent post (but different!)
In my situation I have a 500 kVA, 480V transformer, less than 10' feet away and supplying a 600 amp (frame) instantaneous only (electronic!) breaker that is (let's assume) part of a listed combination controller. (Actually its a VFD). The transformer has NO secondary protection.
What I think is interesting (significant) is that the (electronic!) instantaneous breaker of the starter has an adjustment setting of "1" (i.e. a vertical line at 600amps on the current-time curve). My understanding is that being electronic it's not relying on magnetic forces of an "instantaneous" current.
Can I use this setting of "1" (600amps) to protect my 620amps worth of transformer secondary tap conductors? If set to "1", doesn't this provide the same protection as a electronic breaker with long time, short time, inverse time capabilities (i.e a breaker analogous to a thermal-magnetic breaker)? Is 240.21.(C)(2) fulfilled?