Trench Depth For Conduit Under 4" Concrete Slab

3oFElectric

Member
Location
Tennessee
Occupation
Electrician
If I've got Schedule 40 PVC conduit stubbing up through 4" of concrete slab in single family dwelling, would I be required to trench 12" below the slab per Table 300.5, Column 3, Line 2 even though slab is 4" rather than 2" thick?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Why would you think 4" would be less protection than 2"?
 

3oFElectric

Member
Location
Tennessee
Occupation
Electrician
Actually I'm thinking the opposite. I'd think 4" is more protection and thus wouldn't require me to trench 12" below it because it's thicker than the 2" specified in Table 300.5.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Actually I'm thinking the opposite. I'd think 4" is more protection and thus wouldn't require me to trench 12" below it because it's thicker than the 2" specified in Table 300.5.
👍 Correct.
 

3oFElectric

Member
Location
Tennessee
Occupation
Electrician
I see that under Line 3 of Table 300.5. Would that be if the conduit passes beneath a building or if I stub up into the building? I'd definitely prefer 0" burial depth. But want to be sure of the code requirement in this situation before I start laying down conduit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I see that under Line 3 of Table 300.5. Would that be if the conduit passes beneath a building or if I stub up into the building? I'd definitely prefer 0" burial depth. But want to be sure of the code requirement in this situation before I start laying down conduit.
IMO it's under the building but I'll wait to hear other opinions.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Under the building with 4 in of concrete and a 4 inch pipe your trench would only be the depth of the pipe, cover would be 0 in. Outside of building it seem it would be min trench of 12 inch with 4 inch pipe 4 inch of cover and 4 inch of concrete. as long as no vehicle traffic.
 