Here's a problem I once came upon many presidents ago:
200a 1-ph resi panel. HO complained about dim lights and ceiling fans running slow. I immediately suspected an open neutral in the service, so I opened the panel and took some voltage readings.
On the main lines coming in, I had 242.3V L1-L2.
L1 to ground, 121.5
L2 to ground, 121.3.
So far so good.
But these are the voltages to ground I found in the rest of the panel:
All neutral connections were solid and tight in the neutral bar. 2-pole breakers are highlighted in green. Readings are taken between the breaker terminal and ground.
Anyone wanna take a stab at what I found?
200a 1-ph resi panel. HO complained about dim lights and ceiling fans running slow. I immediately suspected an open neutral in the service, so I opened the panel and took some voltage readings.
On the main lines coming in, I had 242.3V L1-L2.
L1 to ground, 121.5
L2 to ground, 121.3.
So far so good.
But these are the voltages to ground I found in the rest of the panel:
All neutral connections were solid and tight in the neutral bar. 2-pole breakers are highlighted in green. Readings are taken between the breaker terminal and ground.
Anyone wanna take a stab at what I found?