LawnGuyLandSparky said:Why? The diningroom 20a might be the same as the kitchen SABC.
210.52(B)(1) allows it.
LawnGuyLandSparky said:Why? The diningroom 20a might be the same as the kitchen SABC.
I agree with that. It is not explicitly stated in the code that this must be done, but the wording of the code essentially pushes us into this situation.frizbeedog said:At a minimum both of the (SA) circuits must terminate in at least one receptacle for the counter top.
I am not sure what you mean by this. Let me say that once you have the first two SA circuits, and once you have at least one countertop receptacle on each of these first two SA circuits, you can install additional SA circuits, and these additional SA circuits need not supply any countertop receptacles. You can, for example, use one 20 amp circuit to supply nothing other than receptacles in the dining room.frizbeedog said:Whether you require more, or dedicated circuits for specific appliances, or install other allowable outlets on these circuits, they both must hit the countertop at least once.
480sparky said:You don't do to many Vikings, do you? Photo shows two units, one refrigerator, one freezer in a matched, side-by-side configuration.
hillbilly said:Funny thing is....If not for the manufacturer spec.
requiring a dedicated 15A circuit....
That fridge could be on one of the two required small appliance circuits that power the kitchen counter and dining room receptacles.
With a rating of 9.9 amps, the code allows it to be added to a 20A circuit that feeds other receptacles.
If the OP had added only one counter receptacle to the fridge circuit, he would be OK.
Just a opinion
steve
480sparky said:True, but when you've got a HO plopping down 7 figures for a shack in the woods, an couple extra 20a circuits for both the fridge and freezer find their way into the bid awfully easy.:smile:
charlie b said:
I agree with that. It is not explicitly stated in the code that this must be done, but the wording of the code essentially pushes us into this situation.
I am not sure what you mean by this. Let me say that once you have the first two SA circuits, and once you have at least one countertop receptacle on each of these first two SA circuits, you can install additional SA circuits, and these additional SA circuits need not supply any countertop receptacles. You can, for example, use one 20 amp circuit to supply nothing other than receptacles in the dining room.
I don't think that contradicts what you were trying to say. But I wanted to clarify that point.