I figure eventually someone will answer
what do you think is the cause of the discrepancy?
I think it's a problem in the wiring at the jobsite.
could be worse said about some :lol:
I figure eventually someone will answer
what do you think is the cause of the discrepancy?
I figure eventually someone will answer
what do you think is the cause of the discrepancy?
I think it's a problem in the wiring at the jobsite.
the no load readings are moot without the mfgs specI doubt we'll ever get to know now, after a 16 page cage match, I doubt the OP wants to step back into the ring.
Maybe you can tell us? Surely the answer must be in those numbers somewhere?
MTW
The extra 45A is there with the motor uncoupled. The fan plays no part in that.bad fan bearings?
misaligned?
???
The extra 45A is there with the motor uncoupled. The fan plays no part in that.
It will be interesting to see what the motor shop come back with following the motor's return trip there.
Defective motor.explain what would cause this?
You have the nameplate rating of the motor in the first post. It was also stated motor was repaired due to bad bearing.
OL relay will take into account service factor amps so is going to be tripping at 115% of setting.
Don’t see how anyone can defend #2 wire size despite other motors coping with it (and in fact we don’t know wiring to other motors).
Defective motor.
Let's see what the motor shop comes back with.
Maybe they got it wrong. And maybe there is no maybe.motor shop said it was ok, megger, no load i
if bad why send it back?
Maybe they got it wrong. And maybe there is no maybe.
The 153A on no load would ring alarm bells for me.
Shall we be patient and wait to see if they have any new findings?
Patience, Sunshine. Patience.so 152 and 195 no load are both valid numbers?
Patience, Sunshine. Patience.