I figure eventually someone will answer

what do you think is the cause of the discrepancy?

I doubt we'll ever get to know now, after a 16 page cage match, I doubt the OP wants to step back into the ring.

Maybe you can tell us? Surely the answer must be in those numbers somewhere?

MTW
 

JFletcher

Senior Member
Location
Williamsburg, VA
The motor shop could have sent them the specs on a different motor by accident, maybe there meter or the way it reads is substantially different from the site meter, it could even be the motor shop pencil whipped their specs.
 

Ingenieur

Senior Member
Location
Earth
I think it's a problem in the wiring at the jobsite.

he measured the voltage, 480 at pnl, 475 at motor
when calculated using his conductor sizes, lengths and currents 470+
the currents are balanced
wire the same as the 'good' units, the motor was r$r, no wiring change

he said others said it was always like that
what prompted the rebuild (not rewind)?
 

Ingenieur

Senior Member
Location
Earth
I doubt we'll ever get to know now, after a 16 page cage match, I doubt the OP wants to step back into the ring.

Maybe you can tell us? Surely the answer must be in those numbers somewhere?

MTW
the no load readings are moot without the mfgs spec

I think the motor is overloaded at hi speed
the ol's must be turned up since it is running at 115%
125 is allowed but mfgs usually recommend 100% or less, especially with a fixed load
the others are running at 95%+

bad fan bearings?
misaligned?
???
 

Russs57

Senior Member
Location
Miami, Florida, USA
Occupation
Maintenance Engineer
You have the nameplate rating of the motor in the first post. It was also stated motor was repaired due to bad bearing.

OL relay will take into account service factor amps so is going to be tripping at 115% of setting.

Don’t see how anyone can defend #2 wire size despite other motors coping with it (and in fact we don’t know wiring to other motors).
 

Ingenieur

Senior Member
Location
Earth
The extra 45A is there with the motor uncoupled. The fan plays no part in that.
It will be interesting to see what the motor shop come back with following the motor's return trip there.

no load i moot w/o knowing spec and test conditions

again
same motor
same v
same load

30% more current
mostly inductive if no load since motor pf 0.1 range

explain what would cause this?
and why it would not impact lo i?
so no load is hi
hi is hi
but lo is ok
using same coils
 

Ingenieur

Senior Member
Location
Earth
You have the nameplate rating of the motor in the first post. It was also stated motor was repaired due to bad bearing.

OL relay will take into account service factor amps so is going to be tripping at 115% of setting.

Don’t see how anyone can defend #2 wire size despite other motors coping with it (and in fact we don’t know wiring to other motors).

it should only see 145 A for 110'
3.2 v drop

the 'hot' sees 157 or 3.5 v
not an issue

ampacity ~ 115
so runs hot, but so short v drop is not bad
Z will rise running hot but even if doubled only 7 v
the 500 is 2 v max so total worse case drop 10 v or so
result is 267 vs 277 or 3.6% or 462
he measure 274/474 at the motor

I wonder if he meant 2/0?
 

Ingenieur

Senior Member
Location
Earth
Defective motor.
Let's see what the motor shop comes back with.

motor shop said it was ok, megger, no load i
if bad why send it back?

it runs fine on lo
carries the load on hi
and ran like this for 'what I’ve been told this has been and ongoing problem for years'
 

Besoeker

Senior Member
Location
UK
motor shop said it was ok, megger, no load i
if bad why send it back?
Maybe they got it wrong. And maybe there is no maybe.
The 153A on no load would ring alarm bells for me.

Shall we be patient and wait to see if they have any new findings?
 