iwire said:
It is allowed for hanging fixtures

(C) Electric-Discharge Luminaires.
(1) Cord-Connected Installation. A luminaire or a lighting
assembly shall be permitted to be cord connected if the
following conditions apply:

(1) The luminaire is located directly below the outlet or
busway.
(2) The flexible cord meets all the following:
a. Is visible for its entire length outside the luminaire
b. Is not subject to strain or physical damage
c. Is terminated in a grounding-type attachment plug
cap or busway plug, or is a part of a lighting assembly
incorporating a manufactured wiring system
connector in accordance with 604.6(C), or has a
luminaire assembly with a strain relief and canopy
having a maximum 152 mm (6 in.) long section of
raceway for attachment to an outlet box above a
suspended ceiling


I do not think the op was planning on a cord cap and receptacle???
 