frizbeedog
- Oregon
cadpoint said:If you bonded the/a grid would you not be ahead of the minimum ! ? ?
You might be wasting your time since a self contained spa like the one they're talking about doesn't need a grid.
frizbeedog said:You might be wasting your time since a self contained spa like the one they're talking about doesn't need a grid.
I don't believe this is true. The grid is still required. There is no relief for not installing the grid. Perhaps it needs to be put there in case a replacement pump is put in that is not double insulated.frizbeedog said:You might be wasting your time since a self contained spa like the one they're talking about doesn't need a grid.
NEC 2008 680.26(6)(a) said:Double-Insulated Water Pump Motors. Where a double-insulated water pump motor is installed under the provisions of this rule, a solid 8 AWG copper conductor of sufficient length to make a bonding connection to a replacement motor shall be extended from the bonding grid to an accessible point in the vicinity of the pool pump motor. Where there is no connection between the swimming pool bonding grid and the equipment grounding system for the premises, this bonding conductor shall be connected to the equipment grounding conductor of the motor circuit.
M. D. said:Why?? It is outside ,..680.42 (pretty sure no book in front of me) sends us to,.. in part 680.26
In 2008 nec the damn grid needs to be installed under non paved surfaces like grass and such.
I think I understand what you are saying ,.. lets see to make sure .. double insulated pump, plastic everything , nothing to bond to any grid I guess these tubs will have to have a 9in square piece of metal submerged in water ,...so that grid can do something.
Dennis Alwon said:I don't believe this is true. The grid is still required. There is no relief for not installing the grid. Perhaps it needs to be put there in case a replacement pump is put in that is not double insulated.
Yup, and it requires a bonding grid if installed outside ...even if ,as Dennis pointed out ,..it is for the future,.. or as I have pointed out , even if it is just to bond the water .... getting a bit absurd if you ask me.frizbeedog
"At this point I'm not sure what I'm saying. I guess you'd have to define the grid for me. Cause what I thought it was it probably ain't. We are talking about a spa they wheel in, set on the ground and connect to power. Right
The copper grid? 680.26 (B)(1) (b)?"
M. D. said:Yup, and it requires a bonding grid if installed outside ...even ,as Dennis pointed out ,..it is for the future,.. or as I have pointed out , even if it is just to bond the water .... getting a bit absurd if you ask me.
frizbeedog said:"What do you mean I have to move the tub to install a grid?"
Dennis Alwon said:Around here the swimming pool companies do all the bonding and install the pool lights to the brass box.
Dennis Alwon said:And yet another reason why you need to know what your doing before you install a hot tub. Around here the swimming pool companies do all the bonding and install the pool lights to the brass box.
iwire said:Are they using licensed electricians, pulling permits and having the work inspected?
Here only electricians can do electrical work. (Well there are a few exceptions)
Dennis Alwon said:There is a special license for pool companies that they must get that allow s them to do pools only. A very limited license if you will.