Hi all, new to the forum, but getting a lot of good info on a lot of really diverse topics. Thanks to all in advance. My problem is this: I am working on wiring a church that used to be a barroom, and the bar used 120/208 service. There is 120 line to ground each leg on 1 and 2, and 208 to ground on 3. leg to leg there is 240 on all. I do not have any equipment that is going to use the 208, only 120/240. Will it affect the system (meter, transformer, etc.) to simply remove the fuse on the 208 leg and not use it? I can't see where it would hurt, but have never run into this before.I would greatly appreciate any help on this issue. The rest of the work is straightforward commercial installation of lights and power, including package A/C's. Just want to verify my thinking. I'm trying to avoid having to replace the entire service. Thanks again!