Hi Mike-
Is it an "urban myth" that branch feeder wires and branch circuit conductors cannot share the same enclosures (gutters, junctionboxes, etc.) I cannot find a reference in the NEC for this. :-?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Richard
Welcome to the Forum..
change your "feeder" to "service" and look at NEC 230.50
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

Mike is very busy and doesn't very often post here, so I hope you don't mind if I try to answer your question.

So to put it simply, Yes it is an urban myth that feeder conductors and branch circuit conductors can't occupy the same raceway or enclosure.

You can't have service conductors and non service conductors in the same raceway or cable. (See 230.7)

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree, urban legend or electrical urban myth take your pick. For what it's worth there are hundreds of them. :)
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
Welcome to the forum.:)

Mike is very busy and doesn't very often post here, so I hope you don't mind if I try to answer your question.

So to put it simply, Yes it is an urban myth that feeder conductors and branch circuit conductors can't occupy the same raceway or enclosure.

You can't have service conductors and non service conductors in the same raceway or cable. (See 230.7)

Chris

Has Mike-H ever posted here? What is his screen name?
 

physis

Senior Member
Hi Mike-
Is it an "urban myth" that branch feeder wires and branch circuit conductors cannot share the same enclosures (gutters, junctionboxes, etc.) I cannot find a reference in the NEC for this. :-?

So much for them old fashioned breaker panels. :smile:
 