elohr46
Senior Member
- Location
- square one
stickboy1375 said:You have to read your NEC definitions... an outlet is NOT a receptacle.
2005 nec def. receptacle outlet: an outlet where one or more receptacles are installed.
stickboy1375 said:You have to read your NEC definitions... an outlet is NOT a receptacle.
elohr46 said:2005 nec def. receptacle outlet: an outlet where one or more receptacles are installed.
BackInTheHabit said:The laundry circuit IS a dedicated circuit.
stickboy1375 said:This is the way I read it, at least ONE 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s), This circuit shall have no other outlets. I dont see how you can have any thing BUT receptacles on this circuit or anything other than 20 amp receptacle circuits in the laundry room...
Dennis Alwon said:Stickboy, if I run a separate 20 amp branch circuit for the washer that satisfies 210.11(C)(2). No other outlets are installed on this circuit. If I add another receptacle from the lighting circuit I don't see how this would negate 210.11.
Dennis Alwon said:Stickboy, if I run a separate 20 amp branch circuit for the washer that satisfies 210.11(C)(2). No other outlets are installed on this circuit. If I add another receptacle from the lighting circuit I don't see how this would negate 210.11.
stickboy1375 said:One other thing, since when are we providing a receptacle for a washer? We are providing a receptacle for the laundry area.
No it says it shall provide the laundry receptacle outlet(s) required by 210.52(F)it is says you need at least one 20 amp circuit, then it says it shall be provided to supply the laundry receptacle outlet(s).
(F) Laundry Areas. In dwelling units, at least one receptacle outlet shall be installed for the laundry.
Dennis Alwon said:No it says it shall provide the laundry receptacle outlet(s) required by 210.52(F)
stickboy1375 said:I agree, you do need at least ONE, But when we go back to 210.11(C)(2) it clearly says at least one 20amp circuit shall supply the laundry receptacle outlet(s)
what am I missing?
Dennis Alwon said:I believe that is saying that you can more than one on the circuit for the laundry recep. It does not say that all recep. in the laundry must be on that laundry circuit.