Why #12 restricted to 20 amp etc..

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
are you talking about superceding without precise code rule, or something else entirely (not sure I understand )?


If I have been understanding his previous posts on the subject 240.4(D) always applies and there is no specific permission to ignore it at any time.

Am I summing it up right Mark?
 

e57

Senior Member
are you talking about superceding without precise code rule, or something else entirely (not sure I understand )?
Yes many believe you can flatly ignore 240.4(D) if the item served is an air conditioner... Although 240 says A through G. And 240.4(D) says "Specifically" - and I see nothing "specific" in any of the codes listed in G to allow ignoring this - or for any reason.

Anyway - not going to thread-jack - although it is the same topic.... 'limiting small conductor amperage' :roll:
 

e57

Senior Member
If I have been understanding his previous posts on the subject 240.4(D) always applies and there is no specific permission to ignore it at any time.

Am I summing it up right Mark?
Yeah - that about it... Thats me - CODE HERETIC!

Seems we posted at the same time....
 