Why did this fail????????

Status
Not open for further replies.

earlydean

Senior Member
And......don't forget 110.3(B) requires all listed items to be installed according to the instructions.

UL says: "conduit bodies not provided with a volume marking are not intended to enclose splices, taps or devices."
 

realolman

Senior Member
Will it warrant an automatic sneer????????:D


Nah...:smile:... but I think Don_Resqcapt19 and the others have made their point with me.

I will undoubtedly use moguls, troughs, or boxes from now on for more than 3 wires over #6AWG... I guess it's kinda goofy not to, really

... but I would still like someone to 'splain the meaning of 314.28(A)(3).


an' I think I'm done. Good night, Mrs Calabash, wherever you are.:smile:
 

neutral

Senior Member
Location
Missouri
Is it code to put 2 se 2/0 cables in a 3" conduit and LB (PVC) from the meter (320 amp service residental) to 2 200 amp panels. The conduit stops after entering the basement, and the the cables are then routed to the power panels.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
Is it code to put 2 se 2/0 cables in a 3" conduit and LB (PVC) from the meter (320 amp service residental) to 2 200 amp panels. The conduit stops after entering the basement, and the the cables are then routed to the power panels.

Do you meet the minimum bending radius of 338.24?
 