gas pipe bond

Status
Not open for further replies.

NoVA Comms Power

Senior Member
Location
Alexandria, VA
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
jameshot said:
bonding the gas and cold water piping is usually done /allowed at the water heater with 2 clamps and a piece of no 6 copper and meets all the requirements.

Unless you have an electric water heater.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
mark henderson said:
What happens if you loose your grounding electrode? What becomes a ground? With out looking up the code# now It does state DO NOT USE THE GAS PIPE AS A GROUNDING ELECTRODE.
Okay its 250.52b1
How does one bond a gas pipe, yet prevent it from behaving as an electrode "if you loose your grounding electrode"?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Larry,
How does one bond a gas pipe, yet prevent it from behaving as an electrode "if you loose your grounding electrode"?
The gas company takes care of that. If the underground supply pipe in metallic (rare in my area) they install a dielectric fitting between the underground pipe and the meter. This provides electrical isolation for the underground gas pipe and prevents it from becoming an electrode.
Don
 