"Has anyone ever been to a call where OCPDs to other than receptacles have opened without explanation?" LOL! At least a few times a week/month, for the last 40+ years. Amount of lightning plays a role. VFD's are the worst offenders.
Yes! Tell me more about this. Last thing I want is a critical facility tripping OCPDs over a squirrel.
Were the lights 120-277 volts? That will do it considering the pull more current.
"I know it sounds silly, but I want to make sure that absolutely no event internal or external could cause the MCC feeder or main breaker to trip." Doesn't sound silly to me, just unobtainable (but highly admirable on your part). IMHO biggest cause is requirements on ground fault protection on mains, sometimes dependent on rather or not POCO has such protection, but nobody being willing to pay for same protection on downstream stuff.
Unobtainable- well... I'm optimistic. I'm sure there is way. You can't tell me the CIA, Google, Goldman Sachs, Lockheed Martin, Shayne Mountain, Pentagon ect hasn't figured a way to stop everything outside of an actual fault in the zone of protection from clearing just that and nothing more.
What has me stuck is how loads behave on open phase(s), grounded phase(s), sags and zero volts for half to 4 cycles.
Electronic breakers with LSIG protection are great right up to the point where they won't reset at all with no prior warning (and they cost so much in the 100+kAIC variety that nobody wants them sitting on the shelf besides me).
Tell me more about this. I want to avoid breakers and use fuses on everything larger than 225 amps. Some say I'm crazy and maybe I am. But I feel like fuses will beat breakers in many regards. Correct me if I'm wrong.
Once upon a time all my gear (downstream gear too) had main 1A, main 1B and tie breaker 1C plus main 2A, main 2B, tie breaker 2C (draw-out type breakers) with analog panel meters, on both normal and emergency switchboards (in the same room along with multiple ATS's). Every breaker had ground fault modules with visible trip indicators. Made it real easy to see what the problem was and get out of trouble in a hurry. Present management has decided that isn't cost effective to maintain. Heck, some people won't even pay for an extra set of Kirk keys!
Do you really need ground fault protection?
Again, perhaps I am wrong- but in such a case would fused gear not be better? A lot of places have an 'install and forget' policy. Meaning once the gear is installed it does not see a human face for 30 years unless something goes wrong. Or simply only the bare minimum like testing/maintaining the gen and ATS and nothing more.
BTW, I don't do kirk keys. Rivet and label is good :angel:
Best advice I can give is to stop listening to sales people peddling the latest and greatest and go visit the operating engineers and maintenance techs that know what lasts and makes their job easy. Leave the jacket in the car and buy them beers at the local joint where they can feel free to talk.
I'll agree here. But I have to admit drinking Kool-aid from Shaw-mut, Eaton Bussman and Little Fuse has been one of my best experience ever.
Which leads me to ask- after 30 years of not opening, what have you seen fail more: Fused switches like bolted pressures or molded case circuit breakers? What about power circuit breakers?