mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Then your feeder has not been properly designed. Someone used the absolute minimum, or less, to save money.
:?
Then your feeder has not been properly designed. Someone used the absolute minimum, or less, to save money.
Ok, so reading, it appears that even a breaker at 250% may not hold Even if it does, I can't see the MCC feeder holding. :jawdrop:
In post 19, did you use Fig 6 to determine that breakers and feeder protection would not hold?
Refrigeration compressors will stop in 1/4 cycle. I have seen single phase scroll compressors without anti-short cycle protection come back on line running backwards as a consequence of very quick power interruptions.
Breakers over 150-200 amps often have magnetic trip adjustment.
I would say fused stuff requires more maintenance but is maintainable. You have moving parts exposed to local conditions (I'm next to salt water). You have fuse clips that might get loose, etc.
I prefer fuses when they feed one item. I would not use them to feed an entire panel board, mostly because of the possibility of a single phase condition.
Are you aware of the GE Tri-Break line of MCCB's? I have used a lot of them and they might be just what you are looking for. While it is possible to replace fuses they don't make it easy on purpose and it could very well void UL rating. Not even sure if they still make them. If not maybe someone has something like them.
couldn't say what causes an electronic breaker to fail. I would be more inclined to suspect high voltage than low. Some, with outboard modules can be repaired (usually larger draw-out types). If obsolete there are places like Satin America that have retrofits. Others, like Micrologic, you toss in the trash.
I would say fused stuff requires more maintenance but is maintainable. You have moving parts exposed to local conditions (I'm next to salt water). You have fuse clips that might get loose, etc.
Maybe I’m missing something here but pull in is normally around 85 V with 120 V coils and drop out is around 60-75 V based on testing. But more importantly who cares. Once the aux contact drops out the starting circuit drops out in standard 3 wire design. Even 2 wire (PLC) designs are supposed to emulate this. Most PLCs if they drop out turn off outputs on startup.
The biggest problem I see with main breakers is lack of coordination, failed feeder breakers that no longer trip, and somebody didn’t use ground fault in feeder breakers or especially starters. The NEC changes with respect to ground faults and arc flash settings fail to account for coordination so I see a lot of dumb things like having ground fault on the main of an MCC but skipping it in the overloads (cheap to do right, expensive to fix), or instantaneous everywhere (no coordination). The other issue is when you have one huge motor and not much of anything else. Typically the main gets set to 125% of the current while the motor protection is set much higher for obvious reasons so the coordination issue gets missed until startup.
Wouldn't each motor have its own overcurrent protection?Normal power up does not involve the inrush of every motor in a building.
Most buildings are not coordinated. Breakers are left at their factor setting dials and thats it.
I'll also go on a limb and say that a breaker which has not opened in 20 years might take an extra cycle to fully open.
In a hospital environment you are required to have at least two levels of ground fault protection. It is expensive to add GF trip function to fusible switches below 800A.
.The NEC will be requiring 1000A and larger fusible switches to be provided with some type of Arc Flash Energy Reduction switch, it seems many manufacturers will be moving towards incorporating electronics into their fusible switches
Historically 1000A and larger fusible switches require regular (every 3-5 years) operation and maintenance or else the grease, on their moving parts, tends to seize up preventing the switch from opening. A switch stuck in a partially open position can be catastrophic, particularly when trying to clear a single phase event.
For fuses to coordinate, you usually must maintain at least a 2:1 ratio but in other cases it can be as high as 8:1 and the fuses must be from the same manufacturer. What safe guards would be implemented to prevent someone from purchasing 'cheaper' replacement fuses, much less ones from a different manufacturer?
Wouldn't each motor have its own overcurrent protection?
And would they all automatically restart?