    Data Center Power System

    Why do data centers replicate their power systems by 2, 3 or even 4 times? But not hospitals, military bases, pharmaceuticals, waste water ect?


    I'd imagine its not that expensive because only the servers transfer over to the other branch where as none IT loads are just allowed to go down.
    Attached Files

    #2
    Because IT "professionals" think their stuff is super important. And corporate thinks they are omnipotent beings so they go along with whatever they want.

    -Hal

    Comment


      #3
      The diagram you showed is multiple systems for redundancy and is a more efficient way than just a simple duplication.
      3 to make 2 OR 4 to make 3, allow for a virtual "A" system and a "B" system to provide redundant power to the IT equipment and be loaded more than 50% awaiting failover scenarios like a traditional 2N system would have.
      IT servers have the ability to take in dual input sources and most other load types for hospitals, military bases, pharmaceuticals, waste water would need as ATS or MTS to do that. We use an ATS or MTS for HVAC in the data center.
      Ron

      Comment


        #4
        The cost of the extra equipment is far lower than the loss of income that would result from an even short loss of power to the building.
        Charles E. Beck, P.E., Seattle
        Comments based on 2017 NEC unless otherwise noted.

        Comment


          #5
          Originally posted by ron View Post
          The diagram you showed is multiple systems for redundancy and is a more efficient way than just a simple duplication.
          3 to make 2 OR 4 to make 3, allow for a virtual "A" system and a "B" system to provide redundant power to the IT equipment and be loaded more than 50% awaiting failover scenarios like a traditional 2N system would have.
          IT servers have the ability to take in dual input sources and most other load types for hospitals, military bases, pharmaceuticals, waste water would need as ATS or MTS to do that. We use an ATS or MTS for HVAC in the data center.

          Now you've peaked my curiosity. How does this work vs simple duplication?

          Comment


            #6
            In most cases, when the computer center goes down, so does the entire corporation, all remote locations, and roving salesmen with laptops. All manufacturing sites may be able to complete what they're working on. Maybe. Shipping goes down; no sales get completed. No new sales get entered! The cost of losing the data center is massive!

            Click image for larger version

Name:	computer is down do everything manually.jpg
Views:	265
Size:	62.1 KB
ID:	2544677Click image for larger version

Name:	computer is down cook manually food-drink-cook-cooks-chef-kitchens-bad_day-rman2155_low.jpg
Views:	261
Size:	102.8 KB
ID:	2544678

            Comment


              #7
              Originally posted by ron View Post
              We use an ATS or MTS for HVAC in the data center.
              Yup, know exactly what you mean:

              Attached Files

              Comment


                #8
                Originally posted by PaulMmn View Post
                In most cases, when the computer center goes down, so does the entire corporation, all remote locations, and roving salesmen with laptops. All manufacturing sites may be able to complete what they're working on. Maybe. Shipping goes down; no sales get completed. No new sales get entered! The cost of losing the data center is massive!
                Good one, true

                Here is a two on two system: 2 gens, 2 ATS, a tie between each switch-gear after the ATS and multiple ATSs for loads like pumps, chillers, UPS ect. Don't know why but very elegant:

                Attached Files

                Comment


                  #9
                  Originally posted by mbrooke View Post


                  Now you've peaked my curiosity. How does this work vs simple duplication?
                  I’m working from my phone so I don’t have the diagrams handy that I use when working with clients, but this white paper goes over how the installed amount of UPS infrastructure gets to be a lower % closer to the actual critical load starting from 2x equipment (2N or 200%) and working on to 3 to make 2, then 4 to make 3 and on.
                  their language and diagrams just take a little thought to make sense, but it is accurate

                  https://w3.siemens.com/powerdistribu...Redundancy.pdf
                  Ron

                  Comment


                    #10
                    Originally posted by ron View Post

                    I’m working from my phone so I don’t have the diagrams handy that I use when working with clients, but this white paper goes over how the installed amount of UPS infrastructure gets to be a lower % closer to the actual critical load starting from 2x equipment (2N or 200%) and working on to 3 to make 2, then 4 to make 3 and on.
                    their language and diagrams just take a little thought to make sense, but it is accurate

                    https://w3.siemens.com/powerdistribu...Redundancy.pdf
                    When you have time, can you link or send me the client diagrams? I'd be really interested

                    Comment


                      #11
                      Originally posted by mbrooke View Post
                      Why do data centers replicate their power systems by 2, 3 or even 4 times?
                      well the diagram does show pg&e as the utility source.....


                      I would hazard a guess that it is because the amount of money on the line, I cant really think of anywhere but telecom where five 9's is the norm. As a very simple example, google in its entirety brings in about $250k per minute 24/7/365. They will spend whatever it takes to keep the power on. Besides loss of utility power, have to consider everything that could happen inside the building. Need to be able to loose one of pretty much any piece of equipment and still have everything on. Used to work in a DC that had a ATS explode during a monthly test simulating utility outage, only way we knew was the burn marks on the floor the next morning, nothing went down.


                      Hospitals can evacuate. Sewage can be let out in the ocean. Pharmaceutical companies can wait until the power comes back on (although I suppose the downtime would also impact the production rate of bad commercials with too many string lights).


                      Besides the generators and such, the amount of onsite diesel some of these places have onsite is insane. I know of one with only a few gensets that has 90,000 gallons.

                      Comment


                        #12
                        How do they refill that 90,000 gallon farm? How much does it cost?

                        Comment


                          #13
                          Wanting the flow of data over the flow of waste really makes a statement......~RJ~

                          Comment


                            #14
                            Originally posted by romex jockey View Post
                            Wanting the flow of data over the flow of waste really makes a statement......~RJ~
                            Thats because data is the backup. The sewage is piped to Facebook and its servers take care of the rest

                            Comment


                              #15
                              http://www.ccgfacilities.com/pdf/MED...%20CENTERS.pdf
                              [COLOR=#000000]The reports of my death are greatly exaggerated.[/COLOR]