Wondering if it's OK to connect a 208 3ph 230-240Y 112kva transformer to a 3phase subpanel the input current is 100amps
Wondering if it's OK to connect a 208 3ph 230-240Y 112kva transformer to a 3phase subpanel the input current is 100amps
It will feed a 3ph sub panel that is powering a bunch of 240 3ph equipment one is a 100amp welder.
https://www.larsonelectronics.com/p...EVKNXefRoEe8lD45ow9L7KSo5C-rJOZBoCQuwQAvD_BwE
This is the transformer they want me to get. Sorry it a 75kva not 112 that was wrong
It will feed a 3ph sub panel that is powering a bunch of 240 3ph equipment one is a 100amp welder.
https://www.larsonelectronics.com/p...EVKNXefRoEe8lD45ow9L7KSo5C-rJOZBoCQuwQAvD_BwE
This is the transformer they want me to get. Sorry it a 75kva not 112 that was wrong
Larson gave me 2 quotes here is the other one
https://www.larsonelectronics.com/p-147482-.aspx
OK cool. So if they wanted 120 also could I get a transformer that would do that also?
OK cool. So if they wanted 120 also could I get a transformer that would do that also?
So we are trying to keep from running a new service which would entail changing a main panel to a 400amp and doing a hot tap and 200ft of new wire