208 3ph to 230-240 Y transformer

Status
Not open for further replies.

oldsparky52

Senior Member
I'm curious, why that large of a transformer for a 100-amp circuit?

If you have the proper OCP in place, I don't believe the NEC has a problem in under using a transformer's rating. I have heard that transformers might waste more energy when lightly loaded.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It will feed a 3ph sub panel that is powering a bunch of 240 3ph equipment one is a 100amp welder.

https://www.larsonelectronics.com/p...EVKNXefRoEe8lD45ow9L7KSo5C-rJOZBoCQuwQAvD_BwE

This is the transformer they want me to get. Sorry it a 75kva not 112 that was wrong

So I'm guessing that this will be a 3Ø, 3wire, 240 volt system without a neutral? If you need to supply any 120 volt loads then a 3Ø,4W Delta secondary might be better. A 240 volt Wye system has a phase to neutral voltage of 139 volts.
 
Last edited:

Bill 12

Member
Location
Vallejo, ca
So we are trying to keep from running a new service which would entail changing a main panel to a 400amp and doing a hot tap and 200ft of new wire
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Very confusing thread; let's try to clarify:

So you HAVE a 208V 3 phase system, right?

They WANT you to supply their equipment with 240V 3 phase, is that right?

If so, on that 240V system, do they need you to have 120V single phase as well?
 

oldsparky52

Senior Member
So we are trying to keep from running a new service which would entail changing a main panel to a 400amp and doing a hot tap and 200ft of new wire

Have you done a load calculation for the new equipment? Is there room in the existing service load calculation to accept the new loads?

And that 112 kVA transformer is overkill for a 100-amp sub panel.
 