    2500a bussed ct

    does the EC normally install the line side of the bussed CT if its feed from a service gutter?

    #2
    We always do. We just do not connect the Ct's leaving the meter wire for the POCO but we wire the meter pan.

    Here's a 2000 amp service we just did with a 10 point meter pan. Click image for larger version

Name:	20190521_081403.jpg
Views:	1
Size:	142.0 KB
ID:	2380905
    Rob

    Moderator

    All responses based on the 2017 NEC unless otherwise noted

    Comment


      #3
      Weird place for that meter pan and how do you get the cover off that LB?

      -Hal

      Comment


        #4
        Originally posted by hbiss View Post
        Weird place for that meter pan and how do you get the cover off that LB?

        -Hal
        I agree but that was the only place in the closet that the meter pan would fit. The photo is deceiving there is about 6" of space between the LB and the cabinet next to it which was enough room to pull the 10-point meter cable in and install the cover.
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted

        Comment


          #5
          Originally posted by infinity View Post
          . . . 10-point meter cable . . .
          Please tell us more about that cable.
          Master Electrician
          Electrical Contractor
          Richmond, VA

          Comment


            #6
            Originally posted by LarryFine View Post
            Please tell us more about that cable.
            It's a Con Ed specification cable, 10 conductors (10 point) all #9 AWG stranded conductors. Yup that is correct, each conductor is labeled #9 AWG with a special 10-point meter color code.

            Click image for larger version

Name:	20190521_083646.jpg
Views:	1
Size:	144.2 KB
ID:	2380908
            Last edited by infinity; 06-25-19, 11:11 AM. Reason: Added Photo
            Rob

            Moderator

            All responses based on the 2017 NEC unless otherwise noted