A gas pipe? Really?

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Looks more like a BR panel, Siemens boxes are painted with plastic interiors, BR boxes are galvy with steel interiors, & the breakers look like a BR, still good example of hackery.

It is a BR breaker in the image. Good eye! :thumbsup:
 

kwired

Electron manager
Location
NE Nebraska
You said it was abandoned and apparently has some age to it, does it comply with size and length to be a "rod and pipe" electrode or have any insulating protective coatings on it? If it can qualify put a bonding clamp on it and make it look more justified to be done that way:D
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
You said it was abandoned and apparently has some age to it, does it comply with size and length to be a "rod and pipe" electrode or have any insulating protective coatings on it? If it can qualify put a bonding clamp on it and make it look more justified to be done that way:D

All I could determine was what you see in the photo. I don't know if this visible pipe is under pressure or not. The highly finished basement rooms completely cover the pipe. The garage, while having the post WWII visible balsam insulation and knot-less plywood, had no pipe stub, or other hints, like a patched over flue location.

Also, the pipe, at about 12 inches below grade, goes straight through old three-core cement blocks and almost certainly the source of the water infiltration. The home owner is bringing in a pipefitter to work towards the removal of the pipe and water sealing the outside of the concrete block basement wall.
 