The Siemens panel is three years old.
Looks more like a BR panel, Siemens boxes are painted with plastic interiors, BR boxes are galvy with steel interiors, & the breakers look like a BR, still good example of hackery.
Looks more like a BR panel, . . .
You said it was abandoned and apparently has some age to it, does it comply with size and length to be a "rod and pipe" electrode or have any insulating protective coatings on it? If it can qualify put a bonding clamp on it and make it look more justified to be done that way![]()