Is a furnace excluded from GFCI or AFCI requirements? Does it matter if it is in a utility closet or in the garage?
Is a furnace excluded from GFCI or AFCI requirements? Does it matter if it is in a utility closet or in the garage?
If the area the unit is placed is in an area that requires afci or gfci or both then you must have it protected with either or both. There is no exception that I am aware of.
(devils advocate).. Furnace has a factory unit disconnect built-in ad is direct wired with no switch or plug and is in an AFCI required area. Must that circuit be AFCI ?? :
210.12
(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-
ampere branch circuits supplying outlets or devices installed in
dwelling unit kitchens, family rooms, dining rooms, living
rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, laundry areas, or similar rooms or
areas shall be protected by any of the means described in
210.12(A)(1) through (6):
(devils advocate).. Furnace has a factory unit disconnect built-in ad is direct wired with no switch or plug and is in an AFCI required area. Must that circuit be AFCI ?? :
(devils advocate).. Furnace has a factory unit disconnect built-in and is direct wired with no switch or plug and is in an AFCI required area. Must that circuit be AFCI ??
I would have to say yes as the connection to a furnace is an outlet, IMO.
And if it was hardwired from the distribution panel. No box (outlet) !
Run it in GRC.....
~RJ~
That wouldn't relieve the requirement to use AFCI, just would allow it to be located at the first outlet instead of at the beginning of the branch circuit.
But in theory it would meet the intent of the code.
It just omits needing to protect the "home run" with AFCI. Nothing says you can omit AFCI protection for the circuit if there are loads or devices in the rooms mentioned in 210.12(A).
Only exception there is for individual branch circuit supplying a fire alarm system, all other 15-20 amp 120 volt branch circuits must comply regardless of what is supplied. Maybe not what some of us want to hear, but it is what it says.
Nothing in the code- but GRC protects the conductors from being damaged by an over driven staple.
I don't disagree, still must AFCI protect everything at/beyond the first "outlet" of the circuit according to what is written, or put that appliance and any other switching devices in the lines into a room not mentioned in 210.12(A). If in the living room build a closet around it and then it won't need AFCI.
I never said it made sense.
A furnace would be an outlet, correct?
I never said it made sense.