hbiss
EC, Westchester, New York NEC: 2014
- Location
- Hawthorne, New York NEC: 2014
- Occupation
- EC
[B said:PaulMmn[/B]]It all depends... what kinds of arcs do the AFCIs detect? I just had my furnace overhauled last night. It's a fuel oil furnace. Oil is pumped through a spray nozzle into the combustion chamber, where the 120 volt supply is boosted through a transformer to create an electric arc of between 10,000 and 14,000 volts which zaps the oil mist to make sure it ignites. It appears there are two versions-- one with a continuous arc, the other just until the photoelectric sensor sees the light of the burning fuel.
Wont detect an arc on the other side of an isolation transformer, probably not through an autotransformer either.
However AFCI and even GFCI's can be subject to tripping if there is any inductive kickback produced in the application. Which is often kind of random trips rather than predicable trips when this happens.
Actually transformers aren't used anymore for oil burner ignition. I replaced mine several years ago with a small solid-state igniter when the transformer went bad. So I suspect you can expect similar problems to what you experience with gas range igniters.
Most all residential burners use continuous ignition. I'm sure they do make a primary control that will do intermittent ignition like Paul mentions also. In all cases the photo cell monitors the flame to make sure it has ignited and stays ignited. If it doesn't see a flame within 15 seconds of starting and anytime thereafter for 15 seconds, it shuts down the burner and you have to press the reset button. This so you don't have your combustion chamber filled with oil.
-Hal