    Twisted Shielded TC-ER

    Is there something about tc-er cable that prevents it from using twisted shielded wiring. I need the tc-er to cross a class I div 2 boundary to a non hazardous area. I want the twisted shielded because the cable is transporting low voltage differential signals. Cant seem to find the exact cable i want that meets those specifications.
    Time is of the essence, and I am low on essence. ~ Graham Hill

    #2
    Try ITC (Article 727)
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.

    Comment


      #3
      Thanks for the reply. I also need the cable to be rated for festooning, i dont think pltc or itc comes rated for festooning.
      Time is of the essence, and I am low on essence. ~ Graham Hill

      Comment


        #4
        Originally posted by fifty60 View Post
        Thanks for the reply. I also need the cable to be rated for festooning, i dont think pltc or itc comes rated for festooning.
        Why didn't you say that in the beginning? However, both are suitable for festooning, e.g. Section 727.4(6); just contact their manufacturer.
        "Bob"