100 Hp fire pump. about 20' from controller. 208v 3 phase. 280 amps. Would you run 500 mcm or 2 sets of 3/0 in 1- 3"emt. Pump has 1- 3' knockout
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How is the fire pump controller set up? Can it accept parallel conductors? We usually see them as WYE start/Delta run which require 6 conductors to the pump.
 