1 101010 Senior Member Mar 19, 2013 #1 100 Hp fire pump. about 20' from controller. 208v 3 phase. 280 amps. Would you run 500 mcm or 2 sets of 3/0 in 1- 3"emt. Pump has 1- 3' knockout
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Mar 19, 2013 #2 How is the fire pump controller set up? Can it accept parallel conductors? We usually see them as WYE start/Delta run which require 6 conductors to the pump.
C copper chopper Senior Member Location wisconsin Mar 19, 2013 #4 do a cost analysis on both and go with the cheaper one. can you use aluminum wire?