Nec 2014 Article 250.64(D)(2) does not mention bolting them together
Sent from my SM-G935U using Tapatalk
I agree.
It just says no objectionable current.
NEC is not a design manual, and puts that notice in the very front for extraordinary reason.
Remember my take on objectionable current, it's only objectionable if it will cause a problem. If they are not bolted together it May not cause a problem, or when an electrician goes to redo a disconnect he may get shocked by the GEC when he disconnects it, if you have danger label it might not be considered objectionable because he is likely to read it and not get shocked. I would at least have them connected by conductive strut supports or something like that, but again that is design, but design to be NEC compliant. NEC is not a how-to manual, it's a how-not-to