Seal Tight Class I Div 11

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    Seal Tight Class I Div 11

    What are requirements for seal tight in Class 1 Div 2 if any ?

    #2
    Permitted by 501.10(B)(2) for locations where flexibility is required. 501.30(B) will require an equipment bonding jumper of the wire type for the LFMC in most cases.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

    Comment


      #3
      I would add that you need to be sure that it is listed product. Not all LFMC is listed.

      Comment


        #4
        Originally posted by texie View Post
        I would add that you need to be sure that it is listed product. Not all LFMC is listed.
        This is a good point; however, technically, if it isn't listed, it isn't LFMC either. See Section 350.6. Various forms of trade named "Sealtight", "Sealtite", "Seal-tite", "Liquid tight" etc. products may or may not be listed, but it must be listed in order to be LFMC.
        "Bob"
        Robert B. Alexander, P.E.
        Answers based on 2017 NEC unless otherwise noted.