Seal Tight Class I Div 11

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Permitted by 501.10(B)(2) for locations where flexibility is required. 501.30(B) will require an equipment bonding jumper of the wire type for the LFMC in most cases.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I would add that you need to be sure that it is listed product. Not all LFMC is listed.
This is a good point; however, technically, if it isn't listed, it isn't LFMC either. See Section 350.6. Various forms of trade named "Sealtight", "Sealtite", "Seal-tite", "Liquid tight" etc. products may or may not be listed, but it must be listed in order to be LFMC.
 