I have project new building gas station convience store in which utility transformer secondary conductors enter non fuse Disconnect #1 outside convience store building then go to new utility meter/Ct then inside nearest entrance drop to 1000A 208V three phase panelboard. The 1000A panelboard has the grounding electrode system, main bonding jumper.
The engineer when told to move the GEC, main bonding jumper and to provide fuse in Disconnect #1 says Disconnect #1 is required by the local electric utility and is on line side of utility meter contractor to install but utility will own and maintain it and so by NEC 2014 Article 230 is not a service disconnect. No need to move GES and main bonding jumper.
Is the engineer correct? Disconnect #1 would not be serivce disconnect? Has anyone ever heard of such a thing utility disconnect owned and maintain non fuse line side is not considered service disconnect?
Sent from my SM-G935U using Tapatalk
The engineer when told to move the GEC, main bonding jumper and to provide fuse in Disconnect #1 says Disconnect #1 is required by the local electric utility and is on line side of utility meter contractor to install but utility will own and maintain it and so by NEC 2014 Article 230 is not a service disconnect. No need to move GES and main bonding jumper.