Why were neutrals fused in the past? Did code mandate it? And why?


knob-and-tube-IV.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How do you know that there was a fuse in the fuse holder and not a solid conductor?
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
How do you know that there was a fuse in the fuse holder and not a solid conductor?

At one point it was common that there wasn't. I mean, just here, why would someone go through the trouble of running the noodle through an Edison screw holder?
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
It was very common to have fused neutrals. Many of the services were 30 amp 120 volt. 60 amp 120/240 upgrade came along and the old fuse block was refed or left as it was.

Did they ever fuse the noodle at 120/240? Seems like a bad idea, even for the time.
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
According to the 1920 National Electrical Safety Code,

"Grounded neutral conductors in three-wire systems shall be arranged without automatic circuit-breakers or fuses interrupting their continuity, unless the circuit breaker opens all conductors of the circuit with one operation.
In two-wire branches from three-wire circuits the conductor connected to the neutral is not for the purpose of this rule considered a grounded conductor."

I think this meant that the neutral could be fused in 2-wire branch circuits.
Apparently they had circuit breakers back then but not for residential applications.

https://books.google.com/books?id=_...issue 2 "grounded neutral conductors"&f=false
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
The old carter 3w's switched noodles ,treated like the 'hot'

and one did not see anywhere near modern GE's made off them

the more i think about it, the more i suspect metering problems may have existed

~RJ~
 
Last edited:

mbrooke

Batteries Included
Location
United States
Occupation
Technician
According to the 1920 National Electrical Safety Code,

"Grounded neutral conductors in three-wire systems shall be arranged without automatic circuit-breakers or fuses interrupting their continuity, unless the circuit breaker opens all conductors of the circuit with one operation.
In two-wire branches from three-wire circuits the conductor connected to the neutral is not for the purpose of this rule considered a grounded conductor."

I think this meant that the neutral could be fused in 2-wire branch circuits.
Apparently they had circuit breakers back then but not for residential applications.

https://books.google.com/books?id=_P...ors%22&f=false

Thanks :)

But why was it done in the real world? I remember seeing posts where in K&T had fused neutrals, I am positive about this.
 
Last edited:

mbrooke

Batteries Included
Location
United States
Occupation
Technician
IDR coming across more than two circuits, 4 fuses, in older homes and the open knife switch would have been non fused. The picture you posted would have been found in the business district.

Still in very old homes the neutral was fused in 2 wire circuits, and in this one it looks like they wanted to do the same.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Is it possible the fused neutral was from an ungrounded DC service they may have had originally?

I guess not with 3 blades

DC can use a 3-wire system, too. Imagine two batteries in series with the "center tap" brought out with the lines.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Is it possible the fused neutral was from an ungrounded DC service they may have had originally?

I guess not with 3 blades


Maybe. But there was a time in history where fusing the neutral was the standard rather then the exception.


Somehow I doubt folks will believe me unless I post pics...
 

Attachments

  • 120 240 volt fuse box 1.jpg
    120 240 volt fuse box 1.jpg
    62 KB · Views: 23
  • 120 240 volt fuse box 2.JPG
    120 240 volt fuse box 2.JPG
    74.2 KB · Views: 23
  • 120 volt fuse box.jpg
    120 volt fuse box.jpg
    81.6 KB · Views: 22
  • 120240 volt box 3.jpg
    120240 volt box 3.jpg
    65.6 KB · Views: 20
  • exterior 120 volt fuse block.jpg
    exterior 120 volt fuse block.jpg
    75.5 KB · Views: 19
  • fuse board 1.jpg
    fuse board 1.jpg
    80.4 KB · Views: 23
  • IMG_3132.jpg
    IMG_3132.jpg
    111.2 KB · Views: 23
  • IMG_3135.jpg
    IMG_3135.jpg
    127.9 KB · Views: 26

mbrooke

Batteries Included
Location
United States
Occupation
Technician
.....
 

Attachments

  • old Opera House electrical panels___yikes.JPG
    old Opera House electrical panels___yikes.JPG
    112.4 KB · Views: 12
  • seriously hacked up fuse box.jpg
    seriously hacked up fuse box.jpg
    132.9 KB · Views: 15

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Courtesy of Sparky480
 

Attachments

  • user12537_pic2065_1329621948.jpg
    user12537_pic2065_1329621948.jpg
    77.5 KB · Views: 9
  • user12537_pic2066_1329621982.jpg
    user12537_pic2066_1329621982.jpg
    64.8 KB · Views: 10
  • user12537_pic2067_1329621982.jpg
    user12537_pic2067_1329621982.jpg
    81.2 KB · Views: 10
  • user12537_pic2069_1329663901.jpg
    user12537_pic2069_1329663901.jpg
    68.5 KB · Views: 10
  • user12537_pic2070_1329663901.jpg
    user12537_pic2070_1329663901.jpg
    80.9 KB · Views: 11

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Service meter, note the knife blade and fused noodle.
 