Is it permissible to use 12-2-2 NM cable for three switch legs by re-identifying one of the white conductors?
Is it permissible to use 12-2-2 NM cable for three switch legs by re-identifying one of the white conductors?
If used for single-pole, 3-way or 4-way switch loops, the reidentified conductor with white or gray insulation or three continuous white or gray stripes shall be used only for the supply to the switch, but not as a return conductor from the switch to the outlet.
This part of 2014 200.7(C)(1) limits you somewhat:
The use of insulation that is white or gray or that has three continuous white or gray stripes for other than a grounded conductor for circuits of 50 volts or more shall be permitted only as in (1) and (2).
Well, I was responding to your original scenario, which did specify a switch loop. Given the Article 404 requirements you pointed out, the switch loop would require 12-5 or 12-2-3 or something like that which probably doesn't exist.I mean, again considering my exhaust fan / light / heater scenario, just how likely is the use of a Switch Loop anyway.
Well, I was responding to your original scenario, which did specify a switch loop.
I mean, again considering my exhaust fan / light / heater scenario, just how likely is the use of a Switch Loop anyway. I like a 12/4 or a 12-2-2 for the Switched LEGS because it keeps the wire count down in the fan J-box. With the Article 404 neutral requirement, why in the world would I feed the fan, rather than the switch box? I don't need a Switch LOOP, therefor I'm not forced to use the sub part of the 200.7(C) rule.
Read it again, please, Wayne. Rob asked about switched legs, and I responded about switched legs. You then introduced switch loops.
Which company makes 12-4 nm-b? I have not seen it, only 12-2-2.
Yes switch legs, 3 of them plus the neutral conductor, feed is already at the switch. Take the white/red conductor from the 12-2-2 and tape it blue. As dumb as it sounds I believe that this wouldn't be code compliant.
If used for single-pole, 3-way or 4-way switch loops, the reidentified conductor with white or gray insulation or three continuous white or gray stripes shall be used only for the supply to the switch, but not as a return conductor from the switch to the outlet.
Not a switch loop.
The sentence in 200.7(C), that is a PART of the rule, is self-contained, in my opinion. The last part of the "switch loop" sentence applies to the object of that one sentence, i.e., "switch loops"
If this (the "switch loop" sub-rule) applied globally (which IMHO it does not) using two-wire NMB between a two pole thermostat and a 240 Volt electric space heater cannot be allowed.