What about 200.7(C)(1) for re-identifying the 12-2-2 this section also permits a two wire cable to be used for a 240 volt circuit when the white is re-identified.
200.7 Use of Insulation of a White or Gray Color or with
Three Continuous White or Gray Stripes.
(A) General. The following shall be used only for the groun‐
ded circuit conductor, unless otherwise permitted in 200.7(B)
and (C):
(C) Circuits of 50 Volts or More. The use of insulation that is
white or gray or that has three continuous white or gray stripes
for other than a grounded conductor for circuits of 50 volts or
more shall be permitted only as in (1) and (2).
(1) If part of a cable assembly that has the insulation perma‐
nently reidentified to indicate its use as an ungrounded
conductor by marking tape, painting, or other effective
means at its termination and at each location where the
conductor is visible and accessible. Identification shall
encircle the insulation and shall be a color other than
white, gray, or green. If used for single-pole, 3-way or
4-way switch loops, the reidentified conductor with white
or gray insulation or three continuous white or gray
stripes shall be used only for the supply to the switch, but
not as a return conductor from the switch to the outlet.