JS-Addis
Member
- Location
- Addis, Louisiana
My installation is as follows: The source of supply is a 400 amp, 600V, 3-phase safety switch, fused at 400 amps. I have 3 circuits that need to be supplied from this source. Two of the circuits are rated at 150 amps, 480V, 3-phase, and one circuit at 40 amps, 480V, 3-phase.
In lieu of installing a 400 amp feeder with a trough and following the appropriate tap rules for the installation of these circuits can I just connect these circuits to the load side of the power source, of course still utilizing the appropriate tap rules and proper lugs for termination? Or when I connect these circuits to the load side of the power source are they considered feeders not tap conductors?
:?
In lieu of installing a 400 amp feeder with a trough and following the appropriate tap rules for the installation of these circuits can I just connect these circuits to the load side of the power source, of course still utilizing the appropriate tap rules and proper lugs for termination? Or when I connect these circuits to the load side of the power source are they considered feeders not tap conductors?
:?