440.9?

Status
Not open for further replies.

jcross

Member
Location
Piney Flats, TN
Would someone please explain as to what happened to the Article 440.9 proposal, I believe it was for wire type equipment grounding conductors from outdoor disconnect to HVAC units...?? Seems as though as there is a lot of publication about the change, but is was not printed??
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't have a copy of the 2014, just the Draft.
A proposed change referencing Art 350 and 358 was in the Draft. I'm unclear if it made to the Final publication.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
This rule was defeated by a floor motion. The floor motion was made to accept comment 11-28 in the ROC. This comment was to delete the new section 440.9 from the code and the motion passed. The new rule had been accepted at both the proposal and comment stage.

You can go to http://www.nfpa.org/codes-and-standards/document-information-pages?mode=code&code=70
and click on "archived revision information" and scroll down near the bottom to the "association technical meeting" section and click on "transcript" to read the floor discussion on the motion.
 