W wmoreland New member Apr 28, 2009 #1 Do the secondary conductors of a 75 va, 208 volt primary,24 volt secondary control transformer need to be installed in a raceway?
Do the secondary conductors of a 75 va, 208 volt primary,24 volt secondary control transformer need to be installed in a raceway?
Pierre C Belarge Senior Member Location Westchester County, New York Apr 28, 2009 #2 Not as per code, maybe a specification.
Twoskinsoneman Senior Member Location West Virginia, USA NEC: 2020 Occupation Facility Senior Electrician Apr 28, 2009 #3 Pierre C Belarge said: Not as per code, maybe a specification. Click to expand... Why not? Is this control circuit from a class 2 transformer?
Pierre C Belarge said: Not as per code, maybe a specification. Click to expand... Why not? Is this control circuit from a class 2 transformer?
K klrogers2 Member Location Virginia Apr 28, 2009 #4 The transformer described would normally be listed as a class 2 transformer, but of course there will always be exceptions. Kevin
The transformer described would normally be listed as a class 2 transformer, but of course there will always be exceptions. Kevin
Twoskinsoneman Senior Member Location West Virginia, USA NEC: 2020 Occupation Facility Senior Electrician Apr 28, 2009 #5 klrogers2 said: The transformer described would normally be listed as a class 2 transformer, but of course there will always be exceptions. Kevin Click to expand... Got it. I didn't realize that it was a given that it was a class 2. Thanks
klrogers2 said: The transformer described would normally be listed as a class 2 transformer, but of course there will always be exceptions. Kevin Click to expand... Got it. I didn't realize that it was a given that it was a class 2. Thanks