S suemarkp Senior Member Location Kent, WA Occupation Retired Engineer Apr 28, 2009 #1 I just looked at a 480V chiller nameplate and the Minimum Circuit Ampacity is 41.2A. The Max Circuit Breaker rating is 40A. Does that make any sense? Why demand a circuit ampacity larger than the overcurrent protection?
I just looked at a 480V chiller nameplate and the Minimum Circuit Ampacity is 41.2A. The Max Circuit Breaker rating is 40A. Does that make any sense? Why demand a circuit ampacity larger than the overcurrent protection?
R ronmath Senior Member Location Burnsville, MN Apr 29, 2009 #2 I would agree that the unit is not marked correctly. Contact the MFR. for clarification.
R Ragin Cajun Senior Member Location Upstate S.C. Apr 29, 2009 #4 HVAC manufacturers don't make electrical mistakes. It just HAS to be correct!!