I have followed this post with great interest and have decided that post #47 clarifies the intent the best for me. 5-star post by all means. Thanks to all who participated. :smile:
Yes, if you can only get a couple of threads tightened on the conductor, it would be a violation of 110.14 in the sense that it would not be a thorough connection. If I remember correctly, I've seen fittings that crimp around the 300 kcmil and have a point/end that fits in a 4/0 terminal that are listed for the purpose.now all you have to do is locate a 200 amp loadcenter that will accept 300 kcmil wire. :smile:
I've seen fittings that crimp around the 300 kcmil and have a point/end that fits in a 4/0 terminal that are listed for the purpose.![]()
Now that the 'o8 Code has calrifierd the wording of 310.15(B)(6) is the following correct ?
I build a 200 amp serivce, based on the table, I have a 4/0 AL riser.
I feed an outside feed-thru disconnect with my 4/0 AL. I add a 15 amp 2 poe breaker at the outsidepanel and feed an HVAC condensor unit for the gas furnace. I then run a interior feeder to the interior panel for all the other house load. Since the feeder is no longer carrying "all loads associted with he dwelling", it will need to be a 300 kcmil (AL) Correct ?
a 2nd queston. If that outside panel has a 15 amp branch circuit feeding a detached garage (and no condensor) since that garage is "associted with the dwelling" is my house feeder still required to be a 300 kcmil (AL) ?