So how do you plan on handling it? Asume worst case scenario and charge and wire for it or have a sit down with local inspector to gauge his/her interprtation and hope they see it as 215.2 seems to?
Thom, I will tell you this, no matter what we think, Ron our head state inspector says the larger conductor is necessary. I argued with him for 1/2 hr. on it but I was unaware of art. 215.2. Personally I think (uh oh- me thinking) that art. 310.15(B)(6) got changed years ago but no one every changed 215.2. This is a total guess on my part.
I think 215.2 backs up 310.15 (B) (6) in this context.
200amp meter base back to back with 1 200amp panel. The panel would be for all of the appliance and lighting load.
Now if you had a 200amp meter combo feeding 1 200amp panel with ser then you could not use the table for wire size and would need to up size to 350. Reason being the meter combo would void the other panel's standing as being the only one to supply appliance and lighting load.
The only fuzzy thing to me would be if there were a 200amp meter feeding a single 200amp outside disconnect that in turned fed the appliance and lighting panel.
When you stop and add some logical thinking to this, Why would ANY conductor in the building or on the whole property have to be any larger then the SE conductors ? With the exception of derating for temp. or VD.
That is exactly the point we are making. The fact that se cable is used as a feeder inside means the wire must be derated to the 60C and if the entire load of the house is not on the se cable then it cannot have advantage of 310.15(B)(6) and must use 310.15. Thus the wire would have to be a larger conductor size to equal the ampacity of the service conductors.
I'm not so sure the words in the holy scribbling back up the enforcement of what that guy's opinion is:-?:-?:-?
I would think that challange woud fit a majority of the Code changes.I would love to know if there is any documented case where,.. after following article 220 ,. there has been a rash of problems with a 4/0 se cable being used the way that millions are employed right now????
...this Code section provides a different ampacity table
for “3-wire, single-phase dwelling services and feeders.”
Requirements for wire bending space and the conduc-
tor size a terminal is rated to terminate are reduced to
account for the reduced size conductor.
.......NEC Table 310.16 would require 3/0 Copper for 200
A service, while UL 414 would allow 2/0 if marked for
this application [which is in agreement with conductor
ampacities provided in NEC Table 310.15(B)(6)]. These
meter sockets have not been evaluated for applications
that go beyond this limitation.
I would think that challange woud fit a majority of the Code changes.
I'm thinking a line has been crossed:roll:90.1 Purpose
The purpose of this code is the practical safeguarding of persons and property from the hazards arising from the use of electricity.
bump ,. wire bending space ?? resi meter cans ??? reduced ?? terminals ??listed ??
No comments:-?
Yes, this is a holy mess. I brought this whole scenario up before Jan. 1 , 2008 and no one here seemed to think it was an issue. I bet by 2011 some of these issues will be resolved. I hope.
The fact that se cable is used as a feeder inside means the wire must be derated to the 60C and if the entire load of the house is not on the se cable then it cannot have advantage of 310.15(B)(6) and must use 310.15. Thus the wire would have to be a larger conductor size to equal the ampacity of the service conductors.