Is 2-4/0 better??Where did you come up with that size conductor for tapping?
Good question, I wonder how James did?
Is 2-4/0 better??Where did you come up with that size conductor for tapping?
Good question, I wonder how James did?
In my humble opinion, iwire 110.3(B) is pretty weak...
This was actually a good thread.
I wonder how James resolved his dilema????
Matt
Is that Jame's actual job photo or one you found like it?
Well ..... your weak too.
I really don't understand why you think 110.3(B) is 'weak' here.
The conductors are listed and they have cut sheets that describe the make up of those conductors.
Unless you can get the manufacturer to state that they intend the conductors to be split up IMO you have a strong violation of 110.3(B).
(Yeah I know this is old, I have been on the road)
This:
![]()
~Matt
I never said YOU were weak there is no reason to attack me personally.
110.3(B) says I have to install IAW instructions in the listing of labeling.
There are no instructions that says 100% of the strands have to be landed on a single terminal.
If the person who installed this took the time to unravel the wire to land it on multiple terminals, why did he or she still feel the need to cut some of the conductors off?
Your guess is as good as mine - Some people just arent 'cut out' to do the job we do - excuse the pun.
~Matt
Twoskin, you took that way to seriously I was joking around.
I sincerely apologize if you felt I trying to put you down.
Now back to the matter at hand.:smile:
There is a label that says "12 AWG" and 12 AWG is a certain size, when you split it it is no longer 12 AWG and you have definitely not followed the labeling.
First off the code technically says to follow instructions that are in the listing...It doesn't technically say the specs of the item can't be modified.
Also if you split the wire the size of it has not changed. It's still the same area of wire....
When you crimp a wire to mash it flat... It is still the same amount of wire and therefore the wire is still within specs... I really don't see any difference.
You lost me, it says we must use it as labeled.
So we will have to remain in disagreement, I have stated my postion and stand by it.
twoskins, your not showing what the breaker wire ranges are, IMO if the wire is larger than what the listed wire range says, its a violation.Sorry this pick is blurry. The wire is split around a screw that tightens a plate. Does this violate the listing of the wire?
![]()
If the person who installed this took the time to unravel the wire to land it on multiple terminals, why did he or she still feel the need to cut some of the conductors off?