Intrinsically safe circuits going to the tanks for inventory probes and sensors is allowed to be any of the wiring methods suitable for unclassified locations, including those covered by Chapter 7 and Chapter 8. (504.20)
504.70 says the seals (boundary seals) don't need to be explosion proof or flameproof, but need to be identified for the purpose of minimizing passage of gases, vapors, or dusts under normal operating conditions. The exception says Seals shall not be required for enclosures that contain only intrinsically safe apparatus, except as required by 501.15(F)(3) {which deals with drainage in processes which you don't have at gas stations}.
I was speaking with another gas station electrician today and told him as far as I was concerned, running PVC to the intrinsically safe equipment and using PVC boxes was fine. Sealing could be done for the boundaries by using ductseal in the conduits.
He was adamant that I was off base and a hack. I figured I?d throw this out for comments.
504.70 says the seals (boundary seals) don't need to be explosion proof or flameproof, but need to be identified for the purpose of minimizing passage of gases, vapors, or dusts under normal operating conditions. The exception says Seals shall not be required for enclosures that contain only intrinsically safe apparatus, except as required by 501.15(F)(3) {which deals with drainage in processes which you don't have at gas stations}.
I was speaking with another gas station electrician today and told him as far as I was concerned, running PVC to the intrinsically safe equipment and using PVC boxes was fine. Sealing could be done for the boundaries by using ductseal in the conduits.
He was adamant that I was off base and a hack. I figured I?d throw this out for comments.