Nope, Rocky 5.A, 2, & D? Home Alone? :grin:
I'm certainly not arguing or picking on you, just joining in on the discussion. :smile:I agree with that. Its just that in my experience, while anecdodal in nature, is those problems are generally on the white, and generally caused by poor installation from the installer (who is obviously not as cleaver as you), and generally causes the arcing in the wirenut, which I find reduces the life on incandescent lamps. Just trying to contribute![]()
I took the OP to mean that the bulb was working but burning out in a relativly short period of time ie: a week or a few days. If this one light was on a MWBC and the neutral was out is would never work for more than a few seconds. If it was a normal circuit and the neutral was not connected it would have no ill affect on the bulb any more than the switch being turned off.
Ok but still not likely that this one fixture and one other device allowing the 135v is the only 2 loads on the circuit. My point with out going over everything is base on the post the neutral is likely not the problem. If it were a MWBC and it had a 135v across it due to the open neutral there would be other issues in the house thus exposing the issue.
Ok but still not likely that this one fixture and one other device allowing the 135v is the only 2 loads on the circuit. My point with out going over everything is base on the post the neutral is likely not the problem. If it were a MWBC and it had a 135v accross it due to the open neutral there would be other issues in the house thus exposing the issue.
You may be violating code because the pigtail is part of the branch wiring and must be sized according to the breaker on that branch circuit.When Installing multiple lights,Controlled by the same switch .
I pig tail the black & white wires. This way the smaller fixture wire is one on one with the larger switch leg wire & neutral. i think making a better connection.
If a MWBC that had lights and receptacles on it and a loose neutral screw in the SE panel or loose wirenut in a JB the problem may never show itself until the poor connection started to heat during a heavy load, like a portable heater
Then, the 240V would divide across the various resistances that happened to be turned on at the time.
If one phase only had one 100W lamp turned on and the other phase had a 10 A heater turned on, the lamp would have about 221.5V across it and the balance (18.5V) would be felt across the heater.
Again, the problem may never show itself until the heater and that one light was turned on.
But how could you not seperate it to the neutral in this situation...??? I ask!!! :grin:
I understand MWBC its not new, I don't need it explained. My point is this incident was described as having an impact on just one light, and nothing else. If it were a MWBC gone bad it would show itself in more than one place. If there are six lights on the same circuit they would all have the same problem. If there were electronic equipment on that circuit they may be damaged. Since the OP only mentioned one light and did not mention anything else I ruled out the MWBC. In addition to this if it were a MWBC circuit the brightness of the bulb/bulbs would vary depending on the load of the bad MWBC. This was no mentioned by the OP.
Lot of times its the lead coming from the socket to the j-box on the side of the can housing. 9 times out of 10 the two white solid wires are twisted nicely but the little white stranded wire from the can pulls right out of the wire nut.