Feeder ampacity
This is not a tap. The #4/0 are protected at 250 amps, the next standard size up from their ampacity of 230 amps. They feed a 225 amp panel with a 225 amp main, all is good.
I agree, as long as there is a 225 amp main breaker at the panel all is good.
Of course we can supply a 225 amp breaker with a 250 amp feeder.
...230A feeder to be more precise (assuming no ambient or derating adjustment).
NEC 2008 said:
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating no greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
This takes us back to your first post to this thread...
Pierre, Have you been convinced that the original post meets Code ?
I agree with the others if the panel has a 225 main in it.
If the panel is main lug only there is a violation of 408.36
I just read 408.36 again, maybe a little more scrutinizing than in the past.
I was more focused on this train of thought, then the OP's installation.
I guess it is never too late to learn something new...;):cool:
Darn...now I am going to have to go and take all the red tags back from today. Maybe not.:grin: