This is not a tap. The #4/0 are protected at 250 amps, the next standard size up from their ampacity of 230 amps. They feed a 225 amp panel with a 225 amp main, all is good.
...and the 225A CBer in the panel is being supplied by a 250A CBer...this is not permitted.
This is not a tap. The #4/0 are protected at 250 amps, the next standard size up from their ampacity of 230 amps. They feed a 225 amp panel with a 225 amp main, all is good.
I agree, as long as there is a 225 amp main breaker at the panel all is good.
The service has a 400 Amp main with (3) 250A feeder breakers each supplying 4/0 feeders. Each feeder lands on a 225Amp main on a sub-panel.
...230A feeder to be more precise (assuming no ambient or derating adjustment).Of course we can supply a 225 amp breaker with a 250 amp feeder.
NEC 2008 said:408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating no greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
...230A feeder to be more precise.
So are we all Happy. I am..I agree that the install is Okay.
Feel sorry for anyone who got inspected by him today....![]()
Actually I am in a good mood you punks...:grin:
They get red tagged whether or not I am in a good mood.![]()
I agree with the others if the panel has a 225 main in it.
If the panel is main lug only there is a violation of 408.36
I thought the red tags where what puts you in a good mood.
(I know that is not true)
I just read 408.36 again, maybe a little more scrutinizing than in the past.