In a commercial kitchen, is a GFCI device required for a cord-connected coffee pot (NEMA 5-20P) that is NOT located within 6' of a sink but is located on top of a stainless steel counter?
do you know the article? I am having a hard time finding it.
Can the GFI protection come from a GFI breaker in lieu of GFI receptacles?
Can the GFI protection come from a GFI breaker in lieu of GFI receptacles?
Yes.![]()
The circuit is not required to be protected, the receptacles are.
Whatever means you choose to protect the receptacle will work in regards to the NEC, such as GFCI-receptacle, circuit breaker or faceless.
........
They've asked if they can put the protection at the panel in the breakers instead of actually in the receptacles. I couldn't find any reason not too ... so whatever floats their boat in this case!
Thanks again!
GFCI breakers won't work if they plan on using multi-wire branch circuits.
General Purpose: Branch ckt supplying 2 or more recepts for ltg and appliances
Individual: Branch ckt which supplies only one utilization equip.
Multiwire: Branch ckt consisting of 2 or more ungrounded conductors with a voltage between them, and a grounded conductor.
... paraphrased from the Defs of the NEC ... did I paraphrase the Multiwire correctly? Is a 120V general purpose ckt the same as a mutliwire ckt because it has 2 ungrounded conductors and a ground?
I'm working primarily with K-12 schools at this point ... and the circuit will range from conv recepts, 120V/1PH appliances to 277V/3PH appliances (possibly).
General Purpose: Branch ckt supplying 2 or more recepts for ltg and appliances
Individual: Branch ckt which supplies only one utilization equip.
Multiwire: Branch ckt consisting of 2 or more ungrounded conductors with a voltage between them, and a grounded conductor.
... paraphrased from the Defs of the NEC ... did I paraphrase the Multiwire correctly? Is a 120V general purpose ckt the same as a mutliwire ckt because it has 2 ungrounded conductors and a ground?
I'm working primarily with K-12 schools at this point ... and the circuit will range from conv recepts, 120V/1PH appliances to 277V/3PH appliances (possibly).