quogueelectric
- new york
I have always hated the phantom voltage thing. To me there is no such thing it is just that you cant explain properly something you dont understand.
I have always hated the phantom voltage thing. To me there is no such thing it is just that you cant explain properly something you don't understand.
090523-0549 EST
76nemo:
What do you want to measure?
You can measure an 0.001 ohm resistance with a 1500 watt heater and a Fluke 27. This would give you a resolution of better than 1 foot with #12 copper wire.
.[/QUOTE
My 87V measures conductance.
090601-2002 EST
electricalperson:
You have a problem with a ground or neutral somewhere.
If all grounds are connected together at the main panel, and the same for all the neutrals, then I would suggest there is no way you would see 14 V EGC to neutral anywhere with a high impedance meter.
With a high impedance voltmeter measure the voltage between the ground bus and the neutral bus in the main panel. This probably should less than 1 millivolt.
Mount a temporary receptacle at the main panel and connect EGC to the ground bus, and neutral to the neutral bus. Plug a long extension cord into this outlet. The voltage at the end of the extension cord between EGC and neutral with the cord anywhere you go should be not much greater than what you read directly at the main panel.
Go to various outlets and measure the voltage from either or both EGC and neutral of the extension cord to neutral of the outlet being check, and separately to the EGC of the said outlet.
This should allow you to find the circuit that has an open.